To Steptoe, why is an RCD now to be installed, protecting sockets unless in the care of competent people? Although it is classed as additional protection, we must assume the reason is to give closer protection against shock by rapid tripping (40mS instead of 400mS as for a CB or Fuse). You cannot say that it is additional in case the CB or Fuse fails to clear an earth fault, and so you cannot say that the RCD is less reliable than the CB or fuse any more than saying that a CB is more reliable than an RCD.<br />So unless someone gives firm ruling AND logic which no one has as yet, then where are we?<br />Even forgetting the C-Type breakers. I amateurs wired this place and used b-Type breakers and Zs was high then we have the choice of adding local equipotential bonding or adding RCD in addition. We are no by doing the latter RELYING on the RCD solely as suggested by someone's logic, but rather ensuring that shock does not occur. Bad design, I know perfectly well, but who is going to tell the owners that the whole installation is badly designed? and it is!<br />Please don't think I am being argumentative. I am just wanting better logic as to why I am wrong in my logic. Put it this way, if EVERY CB was replaced by an RCBO Zs would not need to comply with Table 41.3!<br />Is there anyone out there who knows how to ask Tony Cable of the NICEIC?<br />He once gave me his card but I cannot find it.<br />Anyone not know who I am referring to?