Hi All, Now here is MY [newbie] understanding of it all. There are TWO elements to circuit protection that we need to worry about. One is disconnection times for shock protection. There is nothing wrong with using an RCD to do this, if Zs is too high for a MCB or fuse to clear the fault in the required time, in fact, there is a bit in the regs that specifically states that this is ok, so Les is PERFECTLY correct in what he says. The second is overcurrent protection. Now, this is where it gets interesting....
ProDave is also perfectly correct too!!!! So far as i know, there is ABSOLUTELY NOTHING in the regs that specify ANY disconnection time requirements WHATSOEVER for a L/N fault, ONLY L/E ones. BUT and this is a GREAT HUGE BIG BUT, as ProDave says, we still need to be mindful of L/N loop impedance so our mcb or fuse can clear the fault in the required time, YES, but in what time?? Well, part of the job of designing a circuit is to check the cable size from the point of view of thermal effects regarding cable heating in the event of a fault.
Now, in the regs, it gives all kinds of tables, [values of "K"] to help us do this, based on the type of cable, the problem is, as it says in the small print, all this is based on a MAXIMUM DISCONNECTION TIME OF FIVE SECONDS, so if our overcurrent protection will not clear the fault in five seconds, then we will have a problem. We will have to work out our own "custom built" value of "K" instead, and i believe this is given in BS 7454 Obviously, this will not be fun. This is why i always check Zs and L/N loop impedance too, because, as pointed out by others, it is perfectly possible for earth loop impedance to be HIGHER than line/neutral loop impedance.. Hope i have not bored you all to death!!! john...