says-les,
The design calculations should have shown up that the Zs for the circuits would have been outside that allowable, thus, the design should have been changed to allow for this by changing the size of the supply cable at least.
If you have a TN-C-S/PME 3ph incoming supply I am surprised that your Zs is outside limits for a C32, @ 0.58 ohms measured.
I would have expected Ze to be around the 0.1 mark, that gives you 0.48 to play with, about 24m of 2.5/1.5 in radial config.
Go to 4/1.5 your up another 4m.
This would give you a ring length based on 2.5/1.5 @ 0.58 ohms & R1+R2 = (r1+r2)/4 of nearly 119m
By your description you have Vigi type units?
In which case why not swap the C32 for a B32?
This would give you 1.16 ohms measured, around 217m of ring length.
That way your Zs will meet the requirements for the MCB & the add on RCD pod will merely be for your additional protection to meet this requirement, not to overcome the poor design and installation practices?
Adding the RCD pods seems a lot more expensive than changing the C32 for a B32!
Taking list prices on Schneider kit even!
I need more insight into your thought process & the installation TBH to understand your point.
The design calculations should have shown up that the Zs for the circuits would have been outside that allowable, thus, the design should have been changed to allow for this by changing the size of the supply cable at least.
If you have a TN-C-S/PME 3ph incoming supply I am surprised that your Zs is outside limits for a C32, @ 0.58 ohms measured.
I would have expected Ze to be around the 0.1 mark, that gives you 0.48 to play with, about 24m of 2.5/1.5 in radial config.
Go to 4/1.5 your up another 4m.
This would give you a ring length based on 2.5/1.5 @ 0.58 ohms & R1+R2 = (r1+r2)/4 of nearly 119m
By your description you have Vigi type units?
In which case why not swap the C32 for a B32?
This would give you 1.16 ohms measured, around 217m of ring length.
That way your Zs will meet the requirements for the MCB & the add on RCD pod will merely be for your additional protection to meet this requirement, not to overcome the poor design and installation practices?
Adding the RCD pods seems a lot more expensive than changing the C32 for a B32!
Taking list prices on Schneider kit even!
I need more insight into your thought process & the installation TBH to understand your point.