Doing a pre-work survey etc, have come across a new one for me..any thoughts appreciated..
1950s house, Ring Main in original 7/.029 & 3/.036. At some point in the past this ring was grossly overloaded as more extensions and spurs including a spur to two huge garden offices were added to the Ring and then someone even added an oven radial with more sockets to the same circuit...etc...
Anyhow apparently when they discovered the end of the ring melted and fused together in the CU..(funny that!) some 'rewiring' was done..what I discovered was that the first legs of the Ring from the CU had been replaced with new 2.5mm T&E but that the rest of the ring had been left with the imperial. No signs of distress or overheating at any of the socket terminations.
The circuit has already been split up etc and now no dangers of overload etc and IR readings >999M. Resistance readings obviously reflect that difference in cable but otherwise all happy.
My question is basically..is there anything Regs-wise or otherwise that would warrant a C3 under an EICR for this mix of size/type cable within the Ring?
cheers
1950s house, Ring Main in original 7/.029 & 3/.036. At some point in the past this ring was grossly overloaded as more extensions and spurs including a spur to two huge garden offices were added to the Ring and then someone even added an oven radial with more sockets to the same circuit...etc...
Anyhow apparently when they discovered the end of the ring melted and fused together in the CU..(funny that!) some 'rewiring' was done..what I discovered was that the first legs of the Ring from the CU had been replaced with new 2.5mm T&E but that the rest of the ring had been left with the imperial. No signs of distress or overheating at any of the socket terminations.
The circuit has already been split up etc and now no dangers of overload etc and IR readings >999M. Resistance readings obviously reflect that difference in cable but otherwise all happy.
My question is basically..is there anything Regs-wise or otherwise that would warrant a C3 under an EICR for this mix of size/type cable within the Ring?
cheers