2391-10 Unit 301 out-come 2
(1) 2.1 / List three human senses that may be used during a periodic inspection :
(2) 2.1 / State which human sense would be most appropriate to identify the following :
i) Loose terminal / connection :
ii) Correct identification of conductor insulation : iii) An overloaded motor winding :
(3) 2.2 / For an initial verification list the individual items to be inspected for an installed domestic consumer unit :
(4) 2.2 / From BS-7671:2008 Schedule of inspections , state the first three checks to be made on an installed cable :
(5) 2.3 / For a periodic inspection list the individual items to be inspected for an installed three-phase distribution board in a motor vehicle workshop :
(6) 2.3 / List the four considerations to be taken into account when deciding the frequency of periodic inspection and testing :
(7) 2.3 / Give two examples of the circumstances that would require a periodic test report :
(8) 2.4 / A periodic inspection report is to be carried out on an existing electrical installation prior to new tenants moving in : State ,
i) What must be agreed with the client before the periodic inspection and test is carried out :
ii) Which document should be agreement in ↔ (i) ↔ be recorded :
iii) One typical example on what might be agreed :
(9) 2.5 / The IEE Guidance Note 3 for competence requires the inspector to have sound knowledge and experience relevant to the nature of the installation being tested : ↔ ( List two other competence requirements ) ↔←←← ******
(10) 2.5 / In order to ensure the safety of persons during the inspection and testing procedure on an installation give three practical measures that would be carried out :
(11) 2.5 / Which statutory document :
i) Places a duty on persons carrying out inspection and testing of electrical installations :
ii) Which two groups of people does the statutory document state that the inspector has a duty to ensure their safety :
(12) 2.5 / State the tile and status given to an inspector in the Electricity at Work regulations 1989 :
Remember Chaps use the right Wording :
2391-10 inspection & testing of Electrical Installations : Unit 301 , Outcome 2 , answers ,
(1) Sight , touch and smell ,
(2) Touch , sight and smell ,
(3)
i) Connection of conductors :
ii) Identification of cables :
iii) Cable selection and size :
iv) Correct connections :
v) Selection and erection to minimise fire :
vi) Basic protection ( IP2X / XXB , IP4X / XXB ) :
vii) Additional protection / RCD type and rating :
ix) Choice and setting of protective devices :
x) Labelling :
xi) Selection of consumer unit appropriate to external influences
(3)
x) Labelling :