A would be buyer gets us to do a PIR on a house . It came out " Unsatisfactory" due to earth rod & lack of RCDs on a TT system .
Noted some readings all over the place on kitchen ring.
Guy buys the place , gets us to do the TT stuff and can we look at kitchen plugs as they keep tripping out .
We'd got the guy to rule out nearly all his appliances from causing tripping .
Main problem seemed to be Mr DIY replacing sockets with flat plate "posh" sockets rammed onto 25mm boxes.
Cables under pressure jammed against the back of the boxes . ( Causing tripping when warm)
Every connection loose.
Earth wire left unconnected.
Spur unit switching the ring leg & not the socket below. ( That threw us ...first we had continuity on the L - L then it was open . ('cos my mate had switched the spur)
Warning should be attached to for DIYers buying flat plate accessories that there may not be enough room .