Disagree canoeboy, Even though it is an MCCB it is still known as a breakerYou still haven't given enough info ?How big are the motors?
Using a contractor for an under voltage relay whilst acceptable is still not good practise, a better method would be an undervoltage monitor in the control circuit with the contactor or an under voltage release on the mccb
The Schneider NSX series is an mccb (moulded case circuit breaker) not a breaker (more often an mcb), ranging from 16 to 630amps with both thermal and magnetic protection.
I do think if you are asking these sort of questions you may well be out of you depth here?
Why do you need an under voltage trip and has the machine been risked assessed for safety to the relevant BS, do you need a proper safety relay, have you thought of PUWER ?