Hi all,
What you make of this??
Overhead TT SP supply
Just about to go out yesterday, when the village idiot turns up moaning that he used something in his garage [remember this] and now all his electrics have tripped off.
I ask, the MCB or an RCD??. He says "both" and that neither will reset...
Ok, so i tell him that, what if you leave the offending MCB off, and then reset the RCD. He says that the RCD will still not reset...
Ok i say, you have got a neutral/earth fault that could be on ANY of the circuits...
I go up there with nothing but a screwdriver i happened to have with me, no means of checking for dead, measuring voltages, or a "neon" or anything, so i was a bit limited in what i could do.
It is an old plastic Mk CU set up as a split load affair. No main switch, the RCD's used as a main switch [Yeah, brilliant, especially on TT] and also, another thing i cannot understand, is why they have got the two RCD's in series, one, [a 100ma TD one] acting as a front end RCD [and also protecting the lighting circuits??] and then a 30mA one protecting the sockets.
Why would you want to do a thing like that?? Myself, i would have a proper DP main switch, and then two 30mA RCD's. No need for a "front end" one, and no need for a 100mA TD one either, but there you go..
Anyway, Here is what i do..
First off, an RCD works by comparing blah blah, you know what i mean, and also, so far as i can remember, the things need more or less mains voltage to operate their own "internals"
So, i switch off the offending MCB. The RCD will not reset.. I take the cable out of the MCB [just in case it was not working] RCD still will not reset..
Ok, so i disconnect the neutral from that circuit. MCB resets.. So, Yehhhh!! was right all along. neutral earth fault on that circuit.. the 100 yard long one feeding his garage.
Now, not wishing to be killed, in between touching anything, i pulled the fuse. AND, as i am not daft and fully aware that the neutral can be very "live" too!! [for various reasons...] i proceeded very carefully.....
Now, wait for this one..... If i disconnected the circuit in questions neutral from the neutral bar, the RCD would reset. The second i went to replace it, [as a test] the RCD tripped, BUT, with the main fuse STILL OUT???
How on earth can an RCD operate when the fuse is pulled.. My opinion is that his installation must have some considerable PD between earth and neutral.. not good.
I did wonder if the cable to the garage [a SWA jobbie] was connected to earth in anyway at the far end, [and hence one possible source of differing potentials] but no, it was not it is terminated in an adaptable box that is waving in fresh air..
Any thoughts?? Everything works normally, so i would think that there is the usual 230 between phase and neutral, so i doubt a DNO neutral fault, so the other idea was that something is livening up his earth and therefore giving a large PD from that on the neutral..
This bloke will NOT spend anything on the house or electrics, and, as i left, he was moaning about "****ty RCD's"
I did point out that if it were not for his one, he would now be dead. Get this!! He had tried to experiment to fix it himself, by digging up his earth rod! as he thought this might stop the RCD tripping....
john...
What you make of this??
Overhead TT SP supply
Just about to go out yesterday, when the village idiot turns up moaning that he used something in his garage [remember this] and now all his electrics have tripped off.
I ask, the MCB or an RCD??. He says "both" and that neither will reset...
Ok, so i tell him that, what if you leave the offending MCB off, and then reset the RCD. He says that the RCD will still not reset...
Ok i say, you have got a neutral/earth fault that could be on ANY of the circuits...
I go up there with nothing but a screwdriver i happened to have with me, no means of checking for dead, measuring voltages, or a "neon" or anything, so i was a bit limited in what i could do.
It is an old plastic Mk CU set up as a split load affair. No main switch, the RCD's used as a main switch [Yeah, brilliant, especially on TT] and also, another thing i cannot understand, is why they have got the two RCD's in series, one, [a 100ma TD one] acting as a front end RCD [and also protecting the lighting circuits??] and then a 30mA one protecting the sockets.
Why would you want to do a thing like that?? Myself, i would have a proper DP main switch, and then two 30mA RCD's. No need for a "front end" one, and no need for a 100mA TD one either, but there you go..
Anyway, Here is what i do..
First off, an RCD works by comparing blah blah, you know what i mean, and also, so far as i can remember, the things need more or less mains voltage to operate their own "internals"
So, i switch off the offending MCB. The RCD will not reset.. I take the cable out of the MCB [just in case it was not working] RCD still will not reset..
Ok, so i disconnect the neutral from that circuit. MCB resets.. So, Yehhhh!! was right all along. neutral earth fault on that circuit.. the 100 yard long one feeding his garage.
Now, not wishing to be killed, in between touching anything, i pulled the fuse. AND, as i am not daft and fully aware that the neutral can be very "live" too!! [for various reasons...] i proceeded very carefully.....
Now, wait for this one..... If i disconnected the circuit in questions neutral from the neutral bar, the RCD would reset. The second i went to replace it, [as a test] the RCD tripped, BUT, with the main fuse STILL OUT???
How on earth can an RCD operate when the fuse is pulled.. My opinion is that his installation must have some considerable PD between earth and neutral.. not good.
I did wonder if the cable to the garage [a SWA jobbie] was connected to earth in anyway at the far end, [and hence one possible source of differing potentials] but no, it was not it is terminated in an adaptable box that is waving in fresh air..
Any thoughts?? Everything works normally, so i would think that there is the usual 230 between phase and neutral, so i doubt a DNO neutral fault, so the other idea was that something is livening up his earth and therefore giving a large PD from that on the neutral..
This bloke will NOT spend anything on the house or electrics, and, as i left, he was moaning about "****ty RCD's"
I did point out that if it were not for his one, he would now be dead. Get this!! He had tried to experiment to fix it himself, by digging up his earth rod! as he thought this might stop the RCD tripping....
john...