Hi,
Doing a board change and came to do r1+r2 on lighting circuit. Theres a cpc in the board but i checked all pendants in the house and there are no visible cpc's. I recon their twisted together above the ceiling like they used to do, but could not access.
What do you guys normally do in this situation. All light fittings are class 2 so i know the esc have guidance for changing a CU with no cpc. Just wanted the quick answer please. Can you put lim on cert or is that a no no as you cant confirm disconnection times without an r1+r2+Ze.
Thanks
Matt
Doing a board change and came to do r1+r2 on lighting circuit. Theres a cpc in the board but i checked all pendants in the house and there are no visible cpc's. I recon their twisted together above the ceiling like they used to do, but could not access.
What do you guys normally do in this situation. All light fittings are class 2 so i know the esc have guidance for changing a CU with no cpc. Just wanted the quick answer please. Can you put lim on cert or is that a no no as you cant confirm disconnection times without an r1+r2+Ze.