need a bit of a push with this as first time i have come across it.
looked at job today, move cooker circuit, hagger cu no rcd, so rcbo, closser look 2.5 mm main earth dissapers somewere underground.
2 incoming water supplies, 1st plastic bonded to first bit off copper 10 mm,
2nd copper and no bonding
ze >299kohms
pefc 1 amp
over head supply
so need to tt or will dno pme it (does any one know the cost)?
so if its tt.
main earth 10mm or even 16 gets mentioned but is that a bit overkill or just a good idear to do.
need to put in rcd, does it need to be time delay 100ma as am putting in 30ma rcbo for cooker. am i right in thinking the cooker needs 30ma rcd as it has a socket outlet
or 30ma rcd to cover all circuits, not ideal i know,
thanks