well it could be 30ma for whole lot100 ma td + 30ma rcbo for cooker circuit that i move

just a thought

30ma for whole lot and one thing trips and it all trips, 100 ma td and a 30ma rcbo cooker, and one thing trips and it all trips, unless its on cooker circuit
yep. if costs are getting prohibitive 1 30ma

 
its a wonder the pikeys are'nt digging them up to weigh in just now.
had one round to day asked if i want my fascia redoing,

 
back on subjet,

so needs rodding sharpish,

30ma rcd cover all circuits unless he wants cu change

inspection pit

10mm earth

whats testing is required for existing circuits, zs +ir or whole lot?

whats daft is he has just brought the place, work has been done, loads of supp bonding in airing cupboad, and no earth

20072010333.jpg

20072010334.jpg

 
6

And I`d do a global (P+N)-E, Ra, and Zs on the cct you`re working on - UNLESS you add a front end RCD.

Then you`ve altered the circuit characteristics, and I`d do an end-of-line Zs, and verify any rings (I`d do that anyway, as I was in the CU.)