Can you explain ...."won't allow to test"
Who or what 'won't allow'?
Who or what 'won't allow'?
Just been to a property that has recently been renovated. Builder has had someone in to extend the main incoming to under the stairs..no earth has been brought through with it..should we put an earth rod in or get the supplier in the thing is they are an old couple who didn't know any better and don't want to get them into trouble..suggestions please thanks in advance
The only sensible [and fairly obvious] thing to do..OR the polarity really IS wrong, hence I would want to check it.
In a similar case once before with no earth, I banged a temporary TT rod in and a wander lead to give me something I actually believed might be "earth" to measure from.
Save messing about with a rod just call the DNOI'm going to put a temporary TT in and call DNO & meter company see what happens..I'm thinking cable damage..Ze is coming back 550...
It is not down to your judgement to create a TNCS connection as the network infrastructure may not be setup to support this, also did you verify the polarity at the service head before doing itmanaged to get 0.16 Zs when piggy back neutral & earth
So do you have the gas connection connected to a true earth or a floating earth point, have you verified whether the gas service pipe metal or plasticbut that's with just the gas connection to earth once I put main earth in from incoming head it reads Polarity voltage
I am not being funny, but i think you are MILES out of your depth here..I'm going to put a temporary TT in and call DNO & meter company see what happens..I'm thinking cable damage..Ze is coming back 550...managed to get 0.16 Zs when piggy back neutral & earth but that's with just the gas connection to earth once I put main earth in from incoming head it reads Polarity voltage
In so doing, they have told you it is TNCS.It's done..DNO came...plate connecting earth to neutral was missing in the incoming head
Or was it an electrician!!!In so doing, they have told you it is TNCS.
So many unanswered questions, like where did the connecting plate go missing in the first place? Why was the original "electrician" so incompetent he did not notice or did not care?
Not sure apparently he suffered a break down client produced paper work to confirm payment of £700 to move incoming....DNO said it must have been jointed and screened over when underfloor heating (water) was installed as there would not of been 3 metres of slack to pull through...british gas turned up to install isolation switch and replaced meterIn so doing, they have told you it is TNCS.
So many unanswered questions, like where did the connecting plate go missing in the first place? Why was the original "electrician" so incompetent he did not notice or did not care?
And cost to client?Not sure apparently he suffered a break down client produced paper work to confirm payment of £700 to move incoming....DNO said it must have been jointed and screened over when underfloor heating (water) was installed as there would not of been 3 metres of slack to pull through...british gas turned up to install isolation switch and replaced meter
Yes....apparently its bee like that since June 22....client said they are going to send a bill back to him...apparently he's living in a B&B in Wales..And cost to client?
Apparently so...they have used him before..said they picked up a flyer @ Taskers for his companyOr was it an electrician!!!
I don't believe the DNO said this do they really believe someone jointed a live service cable it is a ridiculous suggestion.Not sure apparently he suffered a break down client produced paper work to confirm payment of £700 to move incoming....DNO said it must have been jointed and screened over when underfloor heating (water) was installed as there would not of been 3 metres of slack to pull through...british gas turned up to install isolation switch and replaced meter