Hi guys I’m new to this forum I hope you can help. I am an apprentice and while on lockdown I am continuing to study my electrical course. When we come out of lockdown there is job that I will be on with my boss that he has asked me to kind of oversea to help me gain experience and confidence. He has asked me while on lockdown to study the scenario as if it was my own job.
The main incoming fuse is 100A and the Earthing system is a TN-S and it is split via Henley block to which meter tails go to the house and one set of cable goes to an outbuilding. In the out building it goes to an single RCD board. From this board it powers a few circuits in the out building and an outside DB which powers a pond pump and some outside lights. Another distribution board is connected to the outbuilding that goes to a large shed. This is just used to power a few sockets and lighting.
The customer is wanting to run another distribution circuit from the outbuilding to a new building which will be a gym/games room. The Length of cable needed would be 400ft. This new building would need to have 2 rings at 32A and lighting 6A and a some heating 32A.
In the current outbuilding I would change the current RCD board to an RCBO board to prevent unwanted tripping to various DB circuits and make it easier to find a fault in future.
A few questions I just want to clarify .........
As it is a long run of cable ( 400ft) using 16mm2 I would use a 2 core armoured cable ( using an earthing nut on the supply side to earth the steel wire ) to the new building. I would then not earth nut at the new building end but install an earth rod. Would this be the correct thing to do ?
Hope this makes sense. If you need me to give more detail in order for you to help me please let me know. Thanks
The main incoming fuse is 100A and the Earthing system is a TN-S and it is split via Henley block to which meter tails go to the house and one set of cable goes to an outbuilding. In the out building it goes to an single RCD board. From this board it powers a few circuits in the out building and an outside DB which powers a pond pump and some outside lights. Another distribution board is connected to the outbuilding that goes to a large shed. This is just used to power a few sockets and lighting.
The customer is wanting to run another distribution circuit from the outbuilding to a new building which will be a gym/games room. The Length of cable needed would be 400ft. This new building would need to have 2 rings at 32A and lighting 6A and a some heating 32A.
In the current outbuilding I would change the current RCD board to an RCBO board to prevent unwanted tripping to various DB circuits and make it easier to find a fault in future.
A few questions I just want to clarify .........
As it is a long run of cable ( 400ft) using 16mm2 I would use a 2 core armoured cable ( using an earthing nut on the supply side to earth the steel wire ) to the new building. I would then not earth nut at the new building end but install an earth rod. Would this be the correct thing to do ?
Hope this makes sense. If you need me to give more detail in order for you to help me please let me know. Thanks