not noticed that, but I still recon quality of components is main issue.
I won't disagree with that statement
CE mark? Chinese excrament more like
not noticed that, but I still recon quality of components is main issue.
oh right. When measured the gas pipe to the main earthing conductor it’s 700 ohms.ÂIf in any doubt with any metal parts, measure their continuity to earth see if it could be extraneous....
i.e. Think is it possible for this pipe to introduce an earth potential that could provide a path for a current greater than 30ma in the event of a fault..?
e.g. If there was say 4000ohms, (4k), path to electrical earth... Then it has ability to have approx. 60ma fault current!
Basic principle of covering your ar5e....Â
Rather than guess and maybe miss part of the pipe run, where it does actually have some low continuity to earth..
If you have measured, it removes any possibility of you being wrong.
:coffee   Â
oh right. When measured the gas pipe to the main earthing conductor it’s 700 ohms. 
are you adding the fused spur?If say you add an outside light to a fuse spur (3A fuse) when you test it are you just testing from the light to fuse spur or are you testing from the light back to the board. This new light would be the furthest point on the circuit.Â
yes.Âare you adding the fused spur?
what do you think you should test?yes.Â
Â
also am I right in thing installing electrics outside is no longer notifiable in England providing you are not adding a new circuit?Â
RE testing, depends on the age and visual condition of the building , plus the type of cable installed. If it’s VIR, I’ll decline to quote. Are we meant to test the circuit before we do the work before we do the work to check it’s OK but then check after we do the work to to make sure the work that we carry out is safe ? or do people just test after the work.Â
RE testing, depends on the age and visual condition of the building , plus the type of cable installed. If it’s VIR, I’ll decline to quote
 too many variables tbh to give a single answer, then there are lighting circuits which may not have a CPC too ......
ps you would probably do better to start a new topic for each job ...Â
that makes no sense what so ever .... just start a seperate thread, and offer up your thoughts and answer points put to you ....... try it next time, but if you offer no answers and expect to be spoon fed , then don’t be surprised if you get criticisedÂthanks Murdoch - Yes fully appreciate that I should start a new topic but I then get a lot of ‘ you should know that’ when here I have explained that I am really new etc. I really do appreciate all your guys input.Â
thanks Murdoch - Yes fully appreciate that I should start a new topic but I then get a lot of ‘ you should know that’ when here I have explained that I am really new etc. I really do appreciate all your guys input.Â
No fair point. ThanksÂI doubt many people are going to go back a re-read pages of earlier posts to work out your full context and background...
More likely just get confused by a thread supposedly about outbuilding's....?  :C
Ok fair point . I’ll take that on board.Âthat makes no sense what so ever .... just start a seperate thread, and offer up your thoughts and answer points put to you ....... try it next time, but if you offer no answers and expect to be spoon fed , then don’t be surprised if you get criticisedÂ