Right, doing a supply for one of these as a favour so just want to ensure I am covering all the bases as not my normal type of work.
It needs a 16A supply. Assuming it is a PME (Not seen it yet so assuming worst case). SWA to rotary isolator. The jacuzzi is to be treated as a swimming pool as in Section 702. If the isolator is within 2M of the jacuzzi edge then it should be within a class 2 enclosure (702.55.4). The supply must be RCD protected and if a PME requires an earth electrode if the switch is within 2M (702.410.3.4.3). Am I correct in reading that if the switch is further than 2M then the earth electrode bonding is not required? Assuming the main water bonding is satisfactory?
Right, doing a supply for one of these as a favour so just want to ensure I am covering all the bases as not my normal type of work.
It needs a 16A supply. Assuming it is a PME (Not seen it yet so assuming worst case). SWA to rotary isolator. The jacuzzi is to be treated as a swimming pool as in Section 702. If the isolator is within 2M of the jacuzzi edge then it should be within a class 2 enclosure (702.55.4). The supply must be RCD protected and if a PME requires an earth electrode if the switch is within 2M (702.410.3.4.3). Am I correct in reading that if the switch is further than 2M then the earth electrode bonding is not required? Assuming the main water bonding is satisfactory?