PFC on EIC
Mark2spark
Mar 25, 2008
269
Hi Guys, just a 'just wondering' type of question.
When you fill out an EIC, on the PFC bit, what do you put down?
I always use ohms law using the Ze and put down 0.6kA or whatever.
Trainee I am seeing again tomorrow appears to be saying that he's been taught at college to *always* put '6' down, as in 6 kA :shakehead
Hmmm...
6ka???
Just put down the highest measured value PSCC or PEFC
Yeah, 6kA.
Glad it's not just me then :p
How can there be a difference on the 230v supply, of PSCC or PFC then Chris?
(not worded that very well but it's late, sorry)
Mark
PSCC is taken L-N, PEFC is taken L-E, With all bonds connected.
On a TNCS/PME they should be around the same as earth is connected to neutral in the supply head. On TNS, PEFC will usually be lower than PSCC as the earth has a higher resistance. On TT the PEFC will be substantially lower than PSCC as the earth has a higher resistance still.
Been down the pub so that probably doesnt read that well either!!
No that makes perfect sense Chris, thanks for the reply. I didn't think of TN-S systems, I pretty much only do stuff on PME so there's no difference on the 'Nature of Supply Parameters' obviously as N & E are the same thing.
are you sure you dont mean TN-C-S ? ]:)
Yes ;) :innocent
---------- Post Auto-Merged at 22:02 ---------- Previous post was made at 22:01 ----------
Further to my OP:
Well I've cleared it up, trainee was confused, the '6' that is always put down refers to the 6kA limit on breakers :slap