Hello first time on
looking for a bit of advice
I was at a dwelling pricing new consumer unit install in house
When i noticed a container connected to PME
In the house is main consumer unit and connection for container is fed seperatly
The container is fed seperatly by Henley block 16 mm tails to a lewd en box 80 amp fuse and 100 main amp isolation switch
Feed to container is 16 mm armored swa
On checking in container their is a consumer unit with main isolating switch and 63 amp type ac rcd covering 1 no 32 amp wring and 1 no 6 amp lighting circuit
All accessories are plastic
Main earthing terminal is earthed by armored cable earth cable and consumer unit and container connected to it
I do not have much experience in TT installs
Would changing this to tt on container and putting a type s Rcd 100 time delayed at where the connection is in house instead of lewd en cut out switch is be correct way to make this comply
regards
looking for a bit of advice
I was at a dwelling pricing new consumer unit install in house
When i noticed a container connected to PME
In the house is main consumer unit and connection for container is fed seperatly
The container is fed seperatly by Henley block 16 mm tails to a lewd en box 80 amp fuse and 100 main amp isolation switch
Feed to container is 16 mm armored swa
On checking in container their is a consumer unit with main isolating switch and 63 amp type ac rcd covering 1 no 32 amp wring and 1 no 6 amp lighting circuit
All accessories are plastic
Main earthing terminal is earthed by armored cable earth cable and consumer unit and container connected to it
I do not have much experience in TT installs
Would changing this to tt on container and putting a type s Rcd 100 time delayed at where the connection is in house instead of lewd en cut out switch is be correct way to make this comply
regards