^Eh?
Exactly !!As in Zs=Ze+(R1+R2)?But back to the O/P.
Lee: What is the issue? Why bring this up at all? If you`ve got the TX adjacent; then ask the DNO what the supply is. They`ll tell you.
How? Zs = Ze + R1+R2NO, Zs can indeed be lower than Ze,not normally by much though,
are we talking about a normal TN situation here?
in TT it will often be much lower, if you read Ze or Zs and not Ra, this is why an Ra test should be carried out.
pretty much describes most TT installationsTony,I know of an install that has an external earth fault loop impedance of around 160 ohms
The final circuit earth fault loop impedances are around 8 to 9 ohms
in pieces though. his horse & cart cant carry the whole thing in one goDon't be silly he weighs them in.
Is that Ze & ZsTony,I know of an install that has an external earth fault loop impedance of around 160 ohms
The final circuit earth fault loop impedances are around 8 to 9 ohms