Hey guys.
A little question. Say a module has stats of:
Voc - 37.4
Isc - 8.98
Now, obviously these figures are STC values. How do you work out the expected voltage for different temps? Is it to do with the temperature coefficient found on the data sheet?
The reason I ask is this. I was asked today what V would be expect from a string of 16 panels, Now today was about 8 degrees C. The coefficient (Voc) was -0.30 % / degree C
Thus: 25 - 8 = 17 degrees difference from STC
17 * -0.30 = -5.1 = total coefficient
16 x 37.4 = 598.4 Voc for string
598.4 + 5.1% = 628.9v expected
So, why on earth do the physical reading come out at < 550V
What am I missing? (probably something obvious) It could well be down to low irradiance readings, I was told that Volts changes with panel temp. Obviously there must be a point that the generated power is so low to support the voltage????
I'm probably going to be made to look a fool now, but I guess it will get it all out in the air.
Thanks
A little question. Say a module has stats of:
Voc - 37.4
Isc - 8.98
Now, obviously these figures are STC values. How do you work out the expected voltage for different temps? Is it to do with the temperature coefficient found on the data sheet?
The reason I ask is this. I was asked today what V would be expect from a string of 16 panels, Now today was about 8 degrees C. The coefficient (Voc) was -0.30 % / degree C
Thus: 25 - 8 = 17 degrees difference from STC
17 * -0.30 = -5.1 = total coefficient
16 x 37.4 = 598.4 Voc for string
598.4 + 5.1% = 628.9v expected
So, why on earth do the physical reading come out at < 550V
What am I missing? (probably something obvious) It could well be down to low irradiance readings, I was told that Volts changes with panel temp. Obviously there must be a point that the generated power is so low to support the voltage????
I'm probably going to be made to look a fool now, but I guess it will get it all out in the air.
Thanks