Thanks, John.
Apologies if I've misunderstood you, but there isn't any kind of electrical feed going directly to the cabinet; all it is is a metal box that houses rack servers and switches. Each of the servers/switches have their own CPCs. However, some of these servers/switches have a screw terminal on the metal case, which I believe are more for noise reduction rather than for electrical protection.
There is also a lug on the main cabinet for an earth/bonding cable, and then fly-leads that go to the removable side panels and the door of the cabinet.
I just thought it was a case of simply running a cable from the CU to the cabinet, and wasn't really aware of any potential danger.
If the general consensus is that it won't provide any significant advantages, but an increase in danger, then I'll take your advice and will leave things alone.
Thank you to you all for educating me.
I am a dummie where computers are concerned.. I do not know what you mean when you say; "but there isn't any kind of electrical feed going directly to the cabinet; all it is is a metal box that houses rack servers and switches. Each of the servers/switches have their own CPCs"
Whatever these contrivances are, they are powered up from somewhere??
What you must do, is to make sure that you get the earth from the same circuit that powers up this stuff in the box.
It is hard to explain, but a circuit comprises the "live" the neutral, the earth, and devices [breakers, fuses and/or RCCBS] that act together to provide ADS, that is automatic disconnection of supply in the case of an earth fault, this being a fault between a live conductor and earth.
The power has to be shut off a bit sharpish, as all metal parts will be above earth potential for the duration of the fault. This is why you have bonding, so that if your metal fridge has a fault, and the casing rises above earth potential, so does your metal sink, in unison.
This means that if you are touching both at the same time, no current flows through you, as no potential difference between fridge and sink to drive it..
I cannot remember the technical wording, [it is 4am as i write this] but in the same way as you would not take a "live" from one circuit, a neutral from another, you cannot take earths and mix and match them..
Another problem you could have, is it is swings and roundabouts.. Yes, it sounds a great idea to bond the box, but remember this, there is a downside too..
IF you have a fault in the supply to the box, then the ADS should cut the power off very quickly.. The exact time depends on the arrangements for ADS, but it will be a fraction of a second.
However, it is PERFECTLY possible, that due to a fault "out in the street" that your metal box in the garden, could be SERIOUSLY live for days and weeks if bonded to earth from the house..
if it were me, i would be making sure that whatever power went into the box, went through an RCD, absolutely definitely..
I cannot say much more than this, because i do not understand what it is you have in there..
john..