Has anyone else had issues with one of these plug in hot tub units ?
Customer bought one and I installed an outdoor 13a socket for it. When I arrived the plug on the hot tub was a 16a, but all the instructions and the manufacturers website confirmed that this was a 13a unit.
Rang the manufacturer and they said they all go out with these plugs on but yes 13a is correct.
Long story short. 2 failed outdoor sockets later I'm thinking that it does need a 16a socket.
The customer said when the water is changed and the unit has to heat up the plug and socket does get warm.
The rating plate says the unit is 3kw which should be fine but after 2 failed sockets I'm not convinced.
The outdoor socket is on its own 20a rcbo fed with 2.5mm 6242y so no problems on that side of things.
I know the regulations state any item over 2kw should be on its own circuit, but no mention of how these should be connected.
Has anyone else had similar issues ? The outdoor sockets are the BG ones. Never had a problem with any of the others I've put in.
Customer bought one and I installed an outdoor 13a socket for it. When I arrived the plug on the hot tub was a 16a, but all the instructions and the manufacturers website confirmed that this was a 13a unit.
Rang the manufacturer and they said they all go out with these plugs on but yes 13a is correct.
Long story short. 2 failed outdoor sockets later I'm thinking that it does need a 16a socket.
The customer said when the water is changed and the unit has to heat up the plug and socket does get warm.
The rating plate says the unit is 3kw which should be fine but after 2 failed sockets I'm not convinced.
The outdoor socket is on its own 20a rcbo fed with 2.5mm 6242y so no problems on that side of things.
I know the regulations state any item over 2kw should be on its own circuit, but no mention of how these should be connected.
Has anyone else had similar issues ? The outdoor sockets are the BG ones. Never had a problem with any of the others I've put in.