- Oct 22, 2010
- 14,503
- 1,075
Well,that's cleared that up then....they are -they aren't. Schroedingers RCBO?
the little cct diagram on the front of that would suggest single pole
wouldn't expect anything else, but the magic bit is that it isolated nuetral aswell as line.Very clever to get a double pole RCBO into a single module, I'm still a bit sceptical, may have to buy one and take it too bits, looks from the diagram on the side of the unit that it only detects on the L side and the N side is dragged along with the L, the 1∆ is only connected to the L the N does not have its own detection circuit.
tripped loads of RCDs / RCBOs touching neutral to earth, it sees it as an imbalance between neutral and lineThey trip if you touch N to E.
Discovered whilst fault finding yesterday.
Isn't that an approved method of isolation,????tripped loads of RCDs / RCBOs touching neutral to earth, it sees it as an imbalance between neutral and line
I've never done thatIsn't that an approved method of isolation,????
When you're working in an office and nothing is labelled up correctly,It's when the customer goes to reset it and your in the loft or under the floor. Customer reset means turning everything back on.
Of course you would have safely followed the full locking off procedure so that wouldn't be a problem.
You did lock off didn't you ????
This has implies that somewhere an office is labelled correctly!....been on the sauce have weWhen you're working in an office and nothing is labelled up correctly,
LOTO SAVES LIVES
Ahhh is that part of the old wet finger and quick flick test for dead circuits ???good for finding the correct circuit though
Hi Mike, I no longer own SBS Trade Sales, but the single module CRB rcbos are definitely independent 3mm 2 pole switching. Checkout the terminal configuration, two in, two out .And no flying leads. Some others achieve genuine 2 pole by internally switching a neutral flying lead..If you mean does the neutral disconnect at the same time as the phase then yes, but it's because the neutral is dragged along with the phase and not a 3mm gap as far as I know, the only one's I found and used are Hager which are true double pole RCBO's but they are double width, think Legrand do them as well. Forgot to add no earth or fly lead on the Hager.