You may find that even after you have switched off all the MCB's you still get the RCD tripping because there might be a neutral to Earth fault on one of the circuits.
Seriously?Morning guys!
Over the weekend I noticed that the 80a RCD in my consumer unit kept tripping. The house doesn't have anything particularly power hungry - no air con, no DIY tools. It even trips in the middle of the night sometimes (I know so because the house alarm has a little fit when it detects there is no longer any power and switches to the backup battery).
I am wondering what it might be? I replaced the RCD with a second hand one from eBay, seller has 100% feedback and stated it was tested. Is that my issues (I replaced a duff one with a duff one) or is there something else I should look for?
Here's the unit with the switch pointed out. I have a multimeter at the ready to test, just tell me what to target.
Thanks in advance!
I would have started with testing the RCD to see if it is operating correctly first. For this you will need an RCD tested that includes ramp test.
I don't agree that ramp testing is required to verify that an RCD operates correctly. The prescribed tests (half current; I delta n and 5 I delta n) prove this.
prescribed tests are enough, however ramp can sometimes be useful for fault finding.
prescribed tests are enough, however ramp can sometimes be useful for fault finding.
I don't disagree, but they certainly aren't needed to prove whether the RCD is operating correctly. What needs to be remembered is that a 30mA RCD can legitimately operate anywhere between 16mA and 30mA.
I would say say the ramp test is a vital test when looking at random rcd tripping,
as is use of an earth leakage clamp meter ....... but that’s just me ....
Yes .... but if it’s tripping at 16 mA and there is background leakage of, say 15 mA ......
I think you're missing the point. I'm not denying that a ramp test could be useful as a fault finding tool - what I am stating is that it isn't of any use to determine whether an RCD is operating within its parameters or not. That is verified by normal RCD testing, which is precisely why the tests are what they are.
I disagree.
If an RCD has a low threshold, say under 10 mA, then it could be the cause of the tripping ............... if this is not tested , how can it be verified good or not?
The half-current test already proves that it doesn't.
I already said it has merit when fault finding but the proper sequence proves that the RCD is operating within its parameters. So other than fault finding it offers no benefit.Surely if you are fault finding then as many tests as possible will eliminate or locate a potential source of the problem?
A 15mA test proves it's not tripping at 10mA. How are you unconvinced of that incontrovertible fact?not convinced ............. I will keep on doing this test when investigating RCD tripping.
Morning folks. I have been a recommended a good electrician but he is only able to come and see me next Thursday.
While I am waiting I would like to do more fault finding, because the issue is that as soon as the RCD trips, the house alarm goes ballistic because it thinks somebody is trying to bypass it. It went off once at 3am and today at 7am....I apologised to the neighbours by they were not happy (understandably).
Went to bed last night and before doing so, I switched off the 4 x MCBs to the right of the RCD:
1. Electric shower (we never use this, it does work, but we just don't use it)
2. Sockets first floor (on the image it is on, ignore, at the time of going to bed it was down / off)
3. Lights
4. Wall lights
So only the Ring Circuit 1st Floor and Ring Circuit Ground Floor was on. And at 7am, the RCD tripped.
My plan is to repeat the above experiment again, but this time, in addition to having the 4 x MCBs to the right of the RCD in the off position, I shall disconnect anything plugged into the mains ion the 1st floor.
I am wondering if a lose wire is touching the back box or earth? We had some screwless sockets installed about 7 months ago, perhaps that is the cause?
I don't agree that ramp testing is required to verify that an RCD operates correctly. The prescribed tests (half current; I delta n and 5 I delta n) prove this.
I disagree.
If an RCD has a low threshold, say under 10 mA, then it could be the cause of the tripping ............... if this is not tested , how can it be verified good or not?
itll trip in the 1/2 test when it shouldnt. therefore its faulty