The >50V warning should flash and the meter should beep intermittently.
Sounds like Faulty MeterHi again,I've just ran some RCD tests with my Megger.
The touch voltage is shown on a bar graph above the trip time - on each of my tests the graph didn't move, but I am testing on TN-C-S.
I must admit, I've never had a case where the set touch voltage (25v or 50v) has been exceeded on my megger, so I can't say for sure what it would display if this were to happen.
As someone mentioned earlier, though, I can't see how the touch voltage can be exceeded with a Ze of 320 ohms when the calculation for a 50v touch voltage gives us 1667 ohms at 30ma
Bit of a puzzler:C
No mate, I wasn't implying that my meter was wrong - I was comparing things to the Ops problem with his meter.Sounds like Faulty Meter3 Year warranty, they are pretty good at sorting them quickly.