I carried out a cu change today and came across a problem I couldent solve
The sockets are all on 1 ring main throughout the house 2.5mm t&e on a 32a mcb. its a tncs, Ze 0.21 pfc 709
I carried out the dead tests which came out as R1=0.21 Rn=0.22 and R2=0.71Insulation was >500 on live live and >500 on live earth (happy days)
I went live and attempted the zs test, as soon as I pressed the test button the rcd triped. I reset the rcd and tried again with the same out come. I once again reset the rcd and pluged the kettle in the socket. after about 2 seconds it tripped. It seemed to trip every time a load was put onto the circuit. Out of curiosity I wired the ring on the non rcd side and tested the zs. I got a reading of 0.71. Im confused by now.
The last resort was changing the rcd but it had the same outcome. Can anyone suggest the best methods of tracking down the problem as Im very confused on this one, all tests seem fine and it only trips when there is a load added to it.
The sockets are all on 1 ring main throughout the house 2.5mm t&e on a 32a mcb. its a tncs, Ze 0.21 pfc 709
I carried out the dead tests which came out as R1=0.21 Rn=0.22 and R2=0.71Insulation was >500 on live live and >500 on live earth (happy days)
I went live and attempted the zs test, as soon as I pressed the test button the rcd triped. I reset the rcd and tried again with the same out come. I once again reset the rcd and pluged the kettle in the socket. after about 2 seconds it tripped. It seemed to trip every time a load was put onto the circuit. Out of curiosity I wired the ring on the non rcd side and tested the zs. I got a reading of 0.71. Im confused by now.
The last resort was changing the rcd but it had the same outcome. Can anyone suggest the best methods of tracking down the problem as Im very confused on this one, all tests seem fine and it only trips when there is a load added to it.