Right then............. went back today to replace the CU. Did a quick test on the RCD & it failed (didnt trip)
Started taking the wires out the old CU & one of the old fuses had what I thought was a ring circuit connected to it. Did the r1, r2 & rn test & only the r2 had continuity.
Decided to put the 2 lives in seperate RCBO's for now.
Got the rest of the CU up & running, used all RCBO's, & then found when I switched the upstairs landing light on (2 way sw) the RCBO tripped. Took the light down & found no earth but there was an earth at the downstairs & upstairs switches. Did a cont test between the earth at the sw & the neutral at the light & there was 170 ohms. There was no neutral at the upstairs switch so it must been linked from somewhere in the loft but I wasnt able to get up there today. Disconnected the sw live from the upstairs sw & RCBO didnt trip so I think there might be a problem in the loft ?? but....
There is still the problem with the kitchen sockets, tripping the RCBO every time you plug in an appliance. My megger wouldnt even do a Zs on these sockets, just kept saying 'trp' & when I did the RCD test it didnt trip.
Started taking sockets off the wall & got about half way round the kitchen & did a Zs test & the megger read 35 ohms (TT earthing) Is this too high ? because all the other circuits were reading below 1 ohm.
Did the RCD test & all was fine.
So.. I'm left with about 10 sockets disconnected downstream but not left live & I had to leave.
Customer now has half the sockets working in her kitchen.
Could this be related to the problem with the landing light, if maybe there was a borrowed neutral from the sockets for the light & there was an E-N fault on the sw live ?
Blimin long post - sorry - Any suggestions ?
I think I should do an IR test on the remaining sockets not connected at present. Did an IR test before starting, it read about 60M but I didnt think it was anything to worry about.