i still dont agree with you
if the cable is installed to 522.6.6 (i) - (iv), then you can leave it in the wall, anywhere, without RCD protection.
or you can install in a safe zone (522.6.6 (v). however, if its not under supervision of ...., then 522.6.7 states it must be RCD'd.
now if you have a standard T&E in the wall, unprotected (to 522.6.6 (i) - (iv), then it must be installed to 522.6.6 (v) (inside safe zone), which 522.6.7 then says it must be RCD'd.
so if you leave the cable outside the safe zone, you have not complied with 7671
and i still cant see where you got
if the cable is installed to 522.6.6 (i) - (iv), then you can leave it in the wall, anywhere, without RCD protection.
or you can install in a safe zone (522.6.6 (v). however, if its not under supervision of ...., then 522.6.7 states it must be RCD'd.
now if you have a standard T&E in the wall, unprotected (to 522.6.6 (i) - (iv), then it must be installed to 522.6.6 (v) (inside safe zone), which 522.6.7 then says it must be RCD'd.
so if you leave the cable outside the safe zone, you have not complied with 7671
and i still cant see where you got
from?If this is what you intend, I would further suggest that you put this ring on an RCD, as the cables may no longer be in safe zones.