Nicky Tesla
Well-known member
- Joined
- Apr 30, 2008
- Messages
- 1,652
- Reaction score
- 11
Hello, i was on a job the other day when I spotted a seemingly professionally installed CU. It had a NICIEC sticker on it with the cct list with the obvious details such as lighting, conducter size etc, but it never had any columns for any test results such as r1+r2, Zs etc. It did have though was a column for installation method and this was put down as 101 for every cct.
Now not familiar yet with the new method numbers i found out that 101 means installed in insulation in excess of 100mm in the loft, but the only ccts that went through the loft on this newly done rewire was for the upstairs lights, so that cannot be right anyway the others should have been at least a B.
When I was looking in my new OSG it puts 2.5 t&e on the 101 method down at 17A, so this was when i wanted to know if that meant that the cable should have been a 4mm ring cct. In my old yellow regs book the reg no:433-02-04 states " Such ring ccts are deemed to meet the requirements of regulation 433-02-01 if the current carrying capacity(Iz) of the cable is not less than 0.67 times the rated current or current setting of the protective device(In)"
This means that the cable would need to be at least 21A rated, making it require 4mm for the ring.
But I cannot find the above quote in the new regs since they have messed about with the system, so does it still exist or have things changed which now allows this?
Now not familiar yet with the new method numbers i found out that 101 means installed in insulation in excess of 100mm in the loft, but the only ccts that went through the loft on this newly done rewire was for the upstairs lights, so that cannot be right anyway the others should have been at least a B.
When I was looking in my new OSG it puts 2.5 t&e on the 101 method down at 17A, so this was when i wanted to know if that meant that the cable should have been a 4mm ring cct. In my old yellow regs book the reg no:433-02-04 states " Such ring ccts are deemed to meet the requirements of regulation 433-02-01 if the current carrying capacity(Iz) of the cable is not less than 0.67 times the rated current or current setting of the protective device(In)"
This means that the cable would need to be at least 21A rated, making it require 4mm for the ring.
But I cannot find the above quote in the new regs since they have messed about with the system, so does it still exist or have things changed which now allows this?