Hello after some help with an extension of a 32a ring main. I am looking to use two wagoboxs one for each leg of the ring. In each box I would use:
773 -173 41A connections for the Live and Neutral which are both 2.5 mm cables.
222 - 413 24A connections for the Earth cable which is a 1.5mm cable.
This would then in theory de rate the box to 20A which is the minimum allowed for a joint on a ring main.
in theory the Live and Neutral would only be de rated to 32A however due to the use of a 222 connection the over all rating would drop to 20A.
Would this then make the installation MF and comply with the regs?
Happy to discuss!