would you say it was beyond the realms of a tester to ensure compatability?
lostit,
That would depend on the gear you carry and your competence with such large supplies.
Would you have a ductor tester and be able to isolate the bus bars to check the DC resistance?
It is not possible to measure the response to such high fault current levels with any "normal" test gear carried by "normal" sparks.
Most fault response verifications on such systems are by calculation.
Try to make friends with some of the engineers at your local DNO.
I'm lucky, I have a regional office local to me for my DNO and they guys are excellent.
I even have a mobile no. or 2 written down somewhere.
I beleive that you can learn a lot if you get them out for a site assessment and ask the right questions, show respect, and an interest in what they do and, why they do it.
I had an enquiry on a 1600A incomer 11kV sub 5m from consumers origin, tails were double insulated in trench, no armour anywhere.
Could not sort out the earthing, could have been TN-C-S or TN-S.
Spoke to local DNO engineer, he told me if I get the job he'll get the senior linesman over to go in the sub with me to see how they have installed it as it will be quicker and easier than looking up the job records, the building O&M manuals have gone walkies!
Think I've gone a little OT here!