Hello a friend of mine wants to upgrade their shower to a 9.5kw model.
They already have a 6mm shower circuit in place and in use that was installed when the new c/u was fitted, with a 40amp c/b. The cable run is 15 metres and mostly clipped direct apart from the 3 odd metres where it is chased in to a wall. I make this installation reference method B and in the electricians guide to the building regs page 31 table 2.3.1 says a 6mm cable installed ref method B rating is 38amps and on page 49 table 4.1.1 6mm cable should be protected by a 32amp c/b.
I know this was done by 16th edition but was it that different to the 17th edition.
My mate is trying to avoid fitting a new shower cable but wants a bigger shower, but regs says 6mm for showers up to 7.2kw and 10mm for showers up to 9.6kw.
Can anyone shed some light on this please?
They already have a 6mm shower circuit in place and in use that was installed when the new c/u was fitted, with a 40amp c/b. The cable run is 15 metres and mostly clipped direct apart from the 3 odd metres where it is chased in to a wall. I make this installation reference method B and in the electricians guide to the building regs page 31 table 2.3.1 says a 6mm cable installed ref method B rating is 38amps and on page 49 table 4.1.1 6mm cable should be protected by a 32amp c/b.