Right, usually, you have to have an OCPD for a circuit installed at the point where the cable size or current carrying capacity reduces. HOWEVER, you do NOT have to. I cannot remember the reg number, but the OCPD can be within three metres of the point where current carrying capacity reduces, PROVIDED that the chance of anything going wrong in the intervening three metres in low. This is the basis of the rule the DNO's have about max length of tails to be 3 metres. [Remember now, the cutout 1361 is not there to protect the tails, it is there to protect the service cable [bS7671 does not apply to the DNO]
Sooooo, you can use a cable size from the henleys to the shower unit of whatever size you require based on the rating of the OCPD you install in the shower unit and all will be fine. [i am assuming that whatever a Shower unit is, it incorporates an OCPD as well as the RCD]
john....