thats wot hes saying if manafacturers says theres no need then we dont have to fit one,i personally would disagree and say u would have to put on in regardlessDont the 17th say that manufacturers instructions should be followed? Hence if no RCD installed when mfcrs instructions said they should be, means..... electricity + water + accident = lawsuit?
And if the cable is less than 50mm deep in the wall and not protected by a earthed metal plate.Regulation 701.411.3.3In specific locations such as those containing a bath or
shower there is a requirement now to provide RCD
protection on all circuits, including the lighting and shower
circuits.
http://www.voltimum.co.uk/files/gb/others/F/20080903335.pdf
so in a new installation you have to!![]()
Since the 17th ed was introduced..hi all was speaking to my mate the other day and he reckons showers dont have to be rcd protected unless the manafacturer says they should,wot are ur views guys
if u was doing a periodic and the shower had no rcd what code would u put it hasDid you know that there has never, even with the current 17th edition been a requirement for a shower isolator .
Hey Slips I thought any electrical device had to have local isolation ?Did you know that there has never, even with the current 17th edition been a requirement for a shower isolator .
? so what code would u put it as lolBathrooms and shower rooms .....everything on RCD , lights , fans , bubbley wubbley things attached to the bath, what are they called... ... oh yes ..jackonories, and floor heating elements.Deke
So did i. Look it up, but you won't find anything about shower isolators cos it's not there.Hey Slips I thought any electrical device had to have local isolation ?Deke
Except of courseDid you know that there has never, even with the current 17th edition been a requirement for a shower isolator .
I agree, but i said in the 17th edition. You could not really give a code to this on a PIR as it meets BS7671 and unlikely you would have the manufacturers paperwork that came with the unitExcept of course134.1.1 good workmanship.. blah blah.. Manufactures instructions followed..
Shower instruction books normally show a little picture with a
CU, RCD, ISOLATOR, then THE SHOWER.!![]()
![]()
As guidance for the electrical connections.
common sense tells you any competent electrician would be aware of shower manufactures instructions as have been common for many a year now.I agree, but i said in the 17th edition. You could not really give a code to this on a PIR as it meets BS7671 and unlikely you would have the manufacturers paperwork that came with the unit![]()
e.g. if you see smoke coming out of an item of fixed equipment (such as a shower) a local accessible isolator should be present to allow Joe public remove danger.reg 132.15.1 Isolation & switchingEffective means, suitably placed for ready operation, shall be provided so that all voltage may be cut off from every installation, from every circuit thereof and from all equipment, as may be necessary to prevent or remove danger.