Ten four on the special, you learn something new everyday! Now that makes it perfectly clear, Cheers
---------- Post Auto-Merged at 07:33 ---------- Previous post was made at 06:29 ----------
After some toilet thinking!!! Special I understand that... But could I not issue a EIC, or is there a reason why I can't do this for an addition and or alteration in a special location etc? And notify to Part P? Or is there a specific rule where I have to issue a MWC, as this is the confusing part...I think I have been misinterpreted and for that I do apologise.
Part P has nothing to do with the type of certificate issued:-
Part P states certain electrical works or works in certain locations must be notified to the LABC and done in accordance with BS7671..
BS7671 defines what certificates are appropriate for certain types of works
Appendix B of approved document P pages 20 - 34 details the model forms as found in BS7671..
Any person who has passed the relevant C&G's should be aware of which certificates are used where..
(there use used to be in the questions used on exams!)
just to recap....
An EIC can be used for anything and everything to do with installation alterations or additions.....
But if you have only added one accessory onto a circuit..
Then an EIC can have a lot of overkill information..
and loads of bank or N/A boxes..
SO..
To save on wasted space and paper the single sheet MWC covers all the essential detail for small minor aleteration..
But if you had done several minor alterations to multiple circuits...
then it would be more efficient to just do one EIC rather than 3+ MWC's!!!
either way.. both MWC & EIC are applicable to commercial and domestic.
and if domestic and notifiable either can be used dependent upon the works done..
just use the most appropriate one for the job in question....
Horses for courses and all that!
:coffee