If your 2.5/1 didn’t meet the max Zs value, could you then get past this by fitting an RCBO and using it as fault protection as well as additional?
 
So, I was thinking again today (dangerous,I know😂)

If your 2.5/1 didn’t meet the max Zs value, could you then get past this by fitting an RCBO and using it as fault protection as well as additional?

the issue with 2.5/1 is fault current with a 3036 fuse, not Zs, although high Zs is also a problem but a different one
 