I have a Kewtech 103 and the apprentice has my old Rapitest socket tester. Now, we all know that these devices are limited in what they can test. In particular, they are unable to detect neutral / earth reverse polarity. Well, the other day I found another limitation of these testers:
If you have 240v on both line and earth pins, they interpret this as line / neutral reversed.
Had a call from a client who had purchased a new toaster and had got a shock from the casing. He had plugged in his socket tester and it said line / neutral reversed.
So, I went and plugged mine into the toasters socket. Yep, L / N reverse. So, jumped to the [premature] conclusion that this was an open and shut case and that some ejit had miswired the socket.
(that noise you hear is a clanger hitting the floor as I whip off the socket to find the wiring is in fact perfect) :yellow card
Anyway, used the tester to check the other sockets on the circuit (this RFC serves four rooms with 18 sockets) and found a cluster of five sockets in the kitchen displaying this fault.
Using the Megger and testing voltage of pins to MET found that the five faulty sockets had 240 volts on both line and earth pins.
So, there you go. Another limitation of socket testers.
I may do another thread about the actual RFC fault.
If you have 240v on both line and earth pins, they interpret this as line / neutral reversed.
Had a call from a client who had purchased a new toaster and had got a shock from the casing. He had plugged in his socket tester and it said line / neutral reversed.
So, I went and plugged mine into the toasters socket. Yep, L / N reverse. So, jumped to the [premature] conclusion that this was an open and shut case and that some ejit had miswired the socket.
(that noise you hear is a clanger hitting the floor as I whip off the socket to find the wiring is in fact perfect) :yellow card
Anyway, used the tester to check the other sockets on the circuit (this RFC serves four rooms with 18 sockets) and found a cluster of five sockets in the kitchen displaying this fault.
Using the Megger and testing voltage of pins to MET found that the five faulty sockets had 240 volts on both line and earth pins.
So, there you go. Another limitation of socket testers.
I may do another thread about the actual RFC fault.