I am currently installing a 18Kw 3 phase system.
The system has 3 strings of 25
Each panel has an output of 250W
The size of the AC cable on the spec is specified as 25mm from the AC isolator to the 3 Phase MCB.
If my calculations are correct..
18000/(√3x400) = 18000/1.732x400 = 18000/692.8 = 25A ( minus power factor )
So 25A per phase ?
Meaning a 6mm cable would be sufficient?
Any input would be of much help ... Thanks alot guys