Being self employed, and not a member of a scam, it's rare for someone to scrutinise one of my jobs, but they did this week.
It was a timber new build chalet on a private estate. In this case, the estate owner was responsible for providing a supply, in effect making them the DNO. They regularly employ the same firm of electricians to maintain their system and make new connections.
So these other sparks came to make the connection, but unlike a normal DNO wanted to see my EIC (not completed yet, but I was able to show them the hand written schedule of test results)
But before making the connection, they wanted to inspect and test a sample of the circuits, just to make sure.
They were generally happy, apart from 2 things they made me "put right" before they would make the connection. These were:
2 way lighting circuits with 3 core & earth cable. There were a couple of 2 way lighting circuits wired so that all 3 cores of the interlinking cables were live (or switched live). So given that 3c&e is brown, grey and black, and these are all phase colours, I hadn't sleeved them. These guys insisted I sleeved them all brown. My logic is they are all phase colours, so don't need sleeving, their logic is 2 of the cores are L2 and L3 so should be sleeved brown to show they are L1. Who is right?
Off peak CU. Just 2 circuits (2 storage heaters) So this was a small CU with an RCD incomer and two 16A MCB's. These guys insisted I replaced the RCD with a 100A 2 pole switch. I told them the cables were in the walls at less than 50mm so needed RCD protection, but they wouldn't budge, saying they never fit RCD's to storage heaters. So I had to change it to get them to make the connection. Talk about between a rock and a hard place, my installation now no longer meets 17th edition. What would you do?
And the last thing, at the time of their visit, I still had just a few light fittings to connect. So after some basic testing, they unplugged the fuse and took it away again. They came back an hour later, and only when the rest of the light fittings were in place would they make the connection permanent. That I took as a bit of an insult, as they were in effect, not trusting me to isolate a lighting circuit before working on it.
It's a good job all DNO's are not like this.
Anyway, apart from the above, it was good that they had no real problems with my work, and even commented the wiring inside the CU was dressed nicely.
It was a timber new build chalet on a private estate. In this case, the estate owner was responsible for providing a supply, in effect making them the DNO. They regularly employ the same firm of electricians to maintain their system and make new connections.
So these other sparks came to make the connection, but unlike a normal DNO wanted to see my EIC (not completed yet, but I was able to show them the hand written schedule of test results)
But before making the connection, they wanted to inspect and test a sample of the circuits, just to make sure.
They were generally happy, apart from 2 things they made me "put right" before they would make the connection. These were:
2 way lighting circuits with 3 core & earth cable. There were a couple of 2 way lighting circuits wired so that all 3 cores of the interlinking cables were live (or switched live). So given that 3c&e is brown, grey and black, and these are all phase colours, I hadn't sleeved them. These guys insisted I sleeved them all brown. My logic is they are all phase colours, so don't need sleeving, their logic is 2 of the cores are L2 and L3 so should be sleeved brown to show they are L1. Who is right?
Off peak CU. Just 2 circuits (2 storage heaters) So this was a small CU with an RCD incomer and two 16A MCB's. These guys insisted I replaced the RCD with a 100A 2 pole switch. I told them the cables were in the walls at less than 50mm so needed RCD protection, but they wouldn't budge, saying they never fit RCD's to storage heaters. So I had to change it to get them to make the connection. Talk about between a rock and a hard place, my installation now no longer meets 17th edition. What would you do?
And the last thing, at the time of their visit, I still had just a few light fittings to connect. So after some basic testing, they unplugged the fuse and took it away again. They came back an hour later, and only when the rest of the light fittings were in place would they make the connection permanent. That I took as a bit of an insult, as they were in effect, not trusting me to isolate a lighting circuit before working on it.
It's a good job all DNO's are not like this.
Anyway, apart from the above, it was good that they had no real problems with my work, and even commented the wiring inside the CU was dressed nicely.