Hi Guys,
First post here so bear with me on this one.
I've been looking at the 17 th edition dual rcd boards you can buy at the usual sheds and I can't help wondering if the main switch is underated if you use all the mcb's supplied. Heres my logic.
Both RCD's feed from the main switch outlet side.
They come with 4 x 32a, 2 x 16 amp, 3 X 6 amp, 1 x40 amp
Working with diversity for what i would consider a typical install
1st ring downstairs = 32A no diversity allowed
2nd ring upstairs = 40% of 32A=12.8A
3rd ring kitchen = 40% of 32A=12.8A
Assume 4th 32 amp breaker is for 12.5kw cooker= 10A+30% remainder =10A+13A = 23A total
3.5KW immersion @16A = 3500/230 = 15.2A no diversity
2nd 16 amp spare
1st lights D/strs @ 6A @ say 8 x 100W= 800/230=3.5Ax66% = 2.3A
2nd lights u/strs @6A say 6 x100W= 600/230=2.6Ax66%= 1.7A
3rd lights outside @ 6A say 2x500w=1000w/230=4.3x66%=2.9A
Shower @ 40A say 9.5kw=9500/230= 41A no diversity allowed
Add all these up and we get 143.7A potentially through the mainswitch rated @ 100A.
I know we can assume that not all the circuits will be loaded at the same time but it's nearly 50% over the main switch rating.
Am I missing something obvious?
Candleman
First post here so bear with me on this one.
I've been looking at the 17 th edition dual rcd boards you can buy at the usual sheds and I can't help wondering if the main switch is underated if you use all the mcb's supplied. Heres my logic.
Both RCD's feed from the main switch outlet side.
They come with 4 x 32a, 2 x 16 amp, 3 X 6 amp, 1 x40 amp
Working with diversity for what i would consider a typical install
1st ring downstairs = 32A no diversity allowed
2nd ring upstairs = 40% of 32A=12.8A
3rd ring kitchen = 40% of 32A=12.8A
Assume 4th 32 amp breaker is for 12.5kw cooker= 10A+30% remainder =10A+13A = 23A total
3.5KW immersion @16A = 3500/230 = 15.2A no diversity
2nd 16 amp spare
1st lights D/strs @ 6A @ say 8 x 100W= 800/230=3.5Ax66% = 2.3A
2nd lights u/strs @6A say 6 x100W= 600/230=2.6Ax66%= 1.7A
3rd lights outside @ 6A say 2x500w=1000w/230=4.3x66%=2.9A
Shower @ 40A say 9.5kw=9500/230= 41A no diversity allowed
Add all these up and we get 143.7A potentially through the mainswitch rated @ 100A.
I know we can assume that not all the circuits will be loaded at the same time but it's nearly 50% over the main switch rating.
Am I missing something obvious?