409 Where in accordance with Regulation 406 protection against dangerous earth-leakage currents by means of a fuse or overload circuit-breaker is admissible, the means of earthing shall comply with one of the alternative methods set out in Clauses (A)-© below
A) The earthing-lead shall be connected to a means of earthing provided by the supply undertaking which affords a metallic return path to the earthing-point of the supply, either by -
(i) the metal sheath (and armour) of the incoming supply cable;
or (ii) an additional conductor, e.g. a "fifth wire" of an overhead line.
Or (B) Where Protective multiple earthing is carried out by the supply undertaking in accordance with the conditions laid down by the Minister of Fuel and Power with the concurrence of the Postmaster-General (see Appendix F), the earth-continuity conductor, together with the neutral conductor of the consumer's installation, shall be so arranged that connection to the neutral of the incoming supply can be carried out by the supply undertaking.
NOTE 1. - Where earthed concentric wiring is in use in the consumer's installation, the outer metal conductor fulfills the function both of earth-continuity conductor and of neutral conductor.
NOTE 2. - Where the requirements are met by compliance with Clause (B), compliance with Clause © below is desirable as an added precaution.
Or © The earthing-lead shall be connected, at a position as near as practicable to the consumer's terminals, to an effective earth electrode buried in the ground, for example a metal water-pipe system having metal-to-metal joints (see Appendix E) or to a copper strip or rod. Connection to a water-pipe shall be made as near as practicable to its point of entry into the ground. A gas pipe shall not be used as an earth electrode.
NOTE. - Attention is drawn to the increasing use of non-metallic water-pipes and mains, which cannot be used for earthing.