Taking electricity to garage

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
No extraneous metalwork in the garage. So i'll supply the distribution cable to the garage with a 32A RCBO and then fit the garage with just a 100a isolator and the 16A and 6A MCB'S.
Why not a 20A RCBO? might be able to save a few quid on the SWA.

 
So, just to be clear, I protect the supply end with Rcd protection and have no need to bother using RCD protection in the board situated in the garage?

---------- Post Auto-Merged at 13:24 ---------- Previous post was made at 13:23 ----------

Or alternatively have a time delayed at the distribution side

 
I am a little worried with the simple questions being asked are you registered to be able to do this work or are you getting somebody to sign the work off?

 