I think what Unphased is basically saying... {which I agree with..}
When adding brand new circuits or major alterations to an existing circuit you will fully test everything to make sure everything is connected as it should be....
and that all readings and tolerances are within accepted limits.
i.e. Dead tests THEN Live tests..
Whereas:-
With an existing installation {e.g.during a periodic} no mater how much you may want to do...
very few customers would be willing to pay for comprehensive tests of everything!
So the extent and limitations has to be agreed,, this would include the amount of testing that is feasable...
Plus a level of sampling has to be taken anyway.. :C
All you are aiming to establish is if the installation is satisfactory or unsatisfactory and if there are any immediate dangers..
It is not too difficult for a competent person to estimate what the expected values of Zs may typically be...
allowing for type of circuit size of conductors probable parallel bonding paths,..
and if they are within max permited values...
IF readings are getting close to max permitted and/or appear ridiculously high for the type/length of circuit..
then you'd investigate further...
Otherwise you can assume it is reasonably safe without knowing the exact R1+R2!
Back to the Ops original post....
when testing ZS at a bathroom light fitting ( last light in circuit) and a supplementary earth has been connected from the pipe work in 4mm, surely this would give a false Zs reading. Also when carrying out continuity test for the same circuit, guidance note 3 shows placing a link between the earth bar of the consumer unit to the phase conductor ( cct breaker in off position)with supplementary bonding in place, if the cpc of the lighting circuit had become dis-connected say at a light fitting, one would still get a continuity reading and believe that all was fine. i think the cpc for the lighting circuit should be dis-connected from the earth bar and a continuity test may then be carried out without taking the supplementary bonding into account. Also i think a warning notice should be on consumer unit advising that supplementary bonding exists in the bathroom and to dis-connect it for testing purposes. Comments please
If you really want to know the R1+R2 ...
DON'T use the method shown in the GN3 or OSG...
Just take BOTH Line & CPC out of the board and connect them together with a lever Wago connector,...
Then go to your light and read the R1+R2 at the fitting!
WIRING REGULATIONS are NOT black and white instructions...
We all should use our training and skills to establish the best way to gather sufficient information on any particular installtion...
Anyone blankly following the books WILL come unstuck at some point!
I have often used different methods on different installations .....
{I think Mr N Tessla has a few "unorthodox" methods for getting an R1+R2 reading!!! :innocent
especially on a TNCS when N & E are joined at the suppliers cut-out!}
but I couldn't possibly comment :Blushing
:C