Hi All , That was my point from the begining, i always dis-connect the CPC from the earth bar at the consumer unit and connect to the phase conductor,its the only way to be sure of continuity and ignoring parallel earth paths, Thats why i disagree with the procedure in guidance note 3 for continuity of a lighting circuit. (linking earth bar to phase conductor). Also please confirm question i asked before. By connecting a 4mm earth cable to the earth terminal of a bathroom light for supplementary bonding, wouldnt it be possilble for a fault current that may develope at the light fitting to elect to travel down the supplementary earth , thereby passing possibly 100-150 amps of fault current down the pipework and back to the main earth terminal
If you read Guidance Note 3 in context you will find the instructions are correct..
Remember these are the instructions for INITIAL inspection & testing NOT periodic..
and as I said on Post #12...
Go back and read the previous page.. :|
Specifically this bit....
Prior to fixing accessories and bonding straps is the clue..
Fault current.......
As the max Zs for a type B 6A 60898 is 7.67ohms,
The fault current to achieve 0.4second disconnection is {230/7.67} 30A
If a 10A type B circuit it is 4.6ohms,
And this fault current to achieve 0.4second disconnection is {230/4.6} 50A
Any parallel path providing an overall lower resistance down two or more shared routes..
would.....
a) Divide the actual fault current down each leg proportional to their respective resistances
and....
B) Most probably reduce the disconnection time