when testing ZS at a bathroom light fitting ( last light in circuit) and a supplementary earth has been connected from the pipe work in 4mm, surely this would give a false Zs reading. Also when carrying out continuity test for the same circuit, guidance note 3 shows placing a link between the earth bar of the consumer unit to the phase conductor ( cct breaker in off position)with supplementary bonding in place, if the cpc of the lighting circuit had become dis-connected say at a light fitting, one would still get a continuity reading and believe that all was fine. i think the cpc for the lighting circuit should be dis-connected from the earth bar and a continuity test may then be carried out without taking the supplementary bonding into account. Also i think a warning notice should be on consumer unit advising that supplementary bonding exists in the bathroom and to dis-connect it for testing purposes. Comments please