I have an Install where a 16mm 4core has been installed previously. ATM the SWA is coiled up either end At the supply which is a barn converted in to an office for the homeowners business and plant room in new extension to the house. There is no PME available as over head, in the middle of no where and in an earlier life was a farm. My intention is to install a 100mA time delayed RCD at the supply in the office mains room and then a fused switch/switch fuse for the distribution circuit. In the plant room at the end the distribution circuit I want to install a 3 phase DB but this is where it gets a little tricky........All the circuits that need additional protection my means of a 30mA RCD will have to be put on RCBOs however I'm struggling to find single pole switched neutral RCBOs. In a single phase installation I would use SBS compact RCBOs as they are single pole switched neutral but SBS don't do three phase DBs etc. Is any one aware of a brand where I could achieve this or think of another idea? Cheers Lee