Manator
©Honorary Essex Boy™
Hi guys, I did a site survey today in order to carry out periodic testing on a multiple storey building. There are two supplies presented with different earthing arrangements. One is TNS the other TNC-S, initial tests prove that due to the buildings bonding, both earthing arrangements are now joined.
I have never come across this before, so thought I would post up here to see what you all think.
I have not contacted the DNO,I would welcome any constructive idea's.
Background info.
This is a 5 storey building, the TNS supplies three distribution boards, the TNC-S supplies two distribution boards. These boards are situated on each floor via a dry riser system. All supply cables are SWA.
Each floor is cross bonded to steelwork and water. The gas only enters the building on the ground floor and is housed within a purpose built plant room with full auto controls.
Bonding measurements across each earthing system is 0.003 ohms, so they are definitely connected.
Both supplies are three phase 100amp per phase. Main earthing conductors are 25mm copper and connected to an earth bar. All bonding is 16mm copper. For those keen eyed amongst you the earth bar was separated, so that each supply was tested independently.
Any thoughts?
I have never come across this before, so thought I would post up here to see what you all think.
I have not contacted the DNO,I would welcome any constructive idea's.
Background info.
This is a 5 storey building, the TNS supplies three distribution boards, the TNC-S supplies two distribution boards. These boards are situated on each floor via a dry riser system. All supply cables are SWA.
Each floor is cross bonded to steelwork and water. The gas only enters the building on the ground floor and is housed within a purpose built plant room with full auto controls.
Bonding measurements across each earthing system is 0.003 ohms, so they are definitely connected.
Both supplies are three phase 100amp per phase. Main earthing conductors are 25mm copper and connected to an earth bar. All bonding is 16mm copper. For those keen eyed amongst you the earth bar was separated, so that each supply was tested independently.
Any thoughts?