A local AirCon company have the contract for the courts - and just installed a couple of units in a courthouse. They need NIC certs, so asked if I`d go do the I&T for them.
Now, I know what I think about the following - but I`d like to see what y`all think of a couple of things.
The existing installation is PME - they`ve come off a TPN sub-board, (supplied from MCCB@60A/phase)
They`ve installed 2 runs of 5 core SWA - approx 10 metres, and 14 metres respectively.
The runs are to 32A isolators; located directly behind the condensing units - awkward to switch on/off; a damn nightmare to open for testing.
The SWA is then taken from the iso to the condenser unit.
The units are rated 19A per phase each.
The sub board they`ve used is a 12 way TP (type B) ; with these loads already installed:
5 lighting circuits - each on a 10A MCB
1 single phase sub-main, to an unknown location, on a 50A MCB
2 radial socket circuits - each on a 16A MCB
3 ring circuits - each on a 32A MCB
2 SP aircon units, each on a 32A MCB
1 hand dryers circuit - 32A
2 circuits, each with 2 hand dryers on a 20A MCB
1 no. water heater on a 20A MCB and
3 no. water heaters, each on a 16A radial.
The banjos have not been fitted on the DB end.
The glands on the isolators are 20Bs, not Cs.
Oh, and the DB is a merlin (with a mix of merlin and schneider MCBs and RCBos) - the aircon co. have used schneider C32A TPN MCBs
Anybody else foresee a problem???
opcorn
Now, I know what I think about the following - but I`d like to see what y`all think of a couple of things.
The existing installation is PME - they`ve come off a TPN sub-board, (supplied from MCCB@60A/phase)
They`ve installed 2 runs of 5 core SWA - approx 10 metres, and 14 metres respectively.
The runs are to 32A isolators; located directly behind the condensing units - awkward to switch on/off; a damn nightmare to open for testing.
The SWA is then taken from the iso to the condenser unit.
The units are rated 19A per phase each.
The sub board they`ve used is a 12 way TP (type B) ; with these loads already installed:
5 lighting circuits - each on a 10A MCB
1 single phase sub-main, to an unknown location, on a 50A MCB
2 radial socket circuits - each on a 16A MCB
3 ring circuits - each on a 32A MCB
2 SP aircon units, each on a 32A MCB
1 hand dryers circuit - 32A
2 circuits, each with 2 hand dryers on a 20A MCB
1 no. water heater on a 20A MCB and
3 no. water heaters, each on a 16A radial.
The banjos have not been fitted on the DB end.
The glands on the isolators are 20Bs, not Cs.
Oh, and the DB is a merlin (with a mix of merlin and schneider MCBs and RCBos) - the aircon co. have used schneider C32A TPN MCBs
Anybody else foresee a problem???
opcorn