Cu change today, nice and straight forward, posh new tails, new 16mm earth, Bonds to gas and water, 10 way dual RCD MK for an old Wylex rewirables jobby. Easy, NOT!
Did all the usual dead tests with no traumas, popped it all together and energised, hey presto, downstairs lights tripping RCD, ****!
Now I took the trouble to put both lighting circuits on the same side of the board due to past experiences with borrowed neutrals and all that mullarky, so was starting to get thoughtful by this point.
It all meggered out ok, so checked outside lights, (had em full of water before now!) Not them, ****!
Customer saw me head scratching and offered a brew, gratefully accepted, when a strange thing happened. On went the kettle, Out went the RCD again.
Now the ring was on the previously faultless clean side of the board, yet it tripped the RCD on the lighting side.
I'll cut to the chase, Wall lights were fitted some years ago and I'm thinking they've borrowed a neutral from the ring. I was running out of time for any further investigations so have left the lights on PME, all other cicuits on RCD's, for tonight and will return in the morning
What d'ya reckon, It's a teaser!
Bez
Did all the usual dead tests with no traumas, popped it all together and energised, hey presto, downstairs lights tripping RCD, ****!
Now I took the trouble to put both lighting circuits on the same side of the board due to past experiences with borrowed neutrals and all that mullarky, so was starting to get thoughtful by this point.
It all meggered out ok, so checked outside lights, (had em full of water before now!) Not them, ****!
Customer saw me head scratching and offered a brew, gratefully accepted, when a strange thing happened. On went the kettle, Out went the RCD again.
Now the ring was on the previously faultless clean side of the board, yet it tripped the RCD on the lighting side.
I'll cut to the chase, Wall lights were fitted some years ago and I'm thinking they've borrowed a neutral from the ring. I was running out of time for any further investigations so have left the lights on PME, all other cicuits on RCD's, for tonight and will return in the morning
What d'ya reckon, It's a teaser!