Hi There, having looked up the requirements for a transportable unit, i cannot understand the fuss..... Nothing hard to comply with at all. A front end "S" type rcd so all circuits are protected and then standard rcd protection for finals. What is the problem or "onerous" about that?? SWA to a an enclosure with the front end rcd in it, then whatever you like to an ordinary CU, oh and you might have to TT it as no TNCS allowed.

john..

 
I've seen the said building today. It's transportable...as long as they have a very big truck and an even bigger crane.

 