My lecturer says look at the table, all the amp ratings seem to trip at the same time, I just don't understand how to work the table.
Hi Alanz1....
First I just want to say it is really good seeing someone ask a question..
But also put down as much info about what they know and/or think they know as well,
and then asking about what they don't understand...
Rather than far too many who come on here and expect to be spoon-fed answers by just asking what is the answer to 'XYZ'
So good questions so far.. Re the tables..
Some bits of them can be confusing as the scale lines are logarithmic and not linear, and can look a bit strange..
(Some of us older bods still remember using 'log-table-books' during our maths exams!!!)
I dunno if this will help or not...
But you need to know a fuse of circuit breaker will not immediately disconnect the power as soon as the designated current rating is exceeded
And some types of equipment have natural current surges when switching on, which need to be ignored..
whilst other current surges, due to faults, need to be responded to quickly to minimise the risk of electric shock.
So, looking at the table from a different perspective..
For simplicity assume a random circuit with your 25A type D breaker has a 40Amp current flowing.
Along the bottom line (prospective current rms amperes) after the 10A, next line is 20A then 30A then 40A..
follow this line up until it crosses the curved 25A breaker characteristics line..
which is probably somewhere around the 800 seconds line..
(depending on how good your eyes are?!!)
Which suggests with a continual 40A overload fault current it could be 13+ minutes before a type D 25A MCB trips..
So in your case with a 380+ Amps fault current you need to guestimate whereabouts a line proportional to 383amps would cross the curved 25A breaker line and go horizontally to see what time duration that would be...
BUT.. if you are looking for a 0.4disconnection time...
most sensible people just look at the table on the right hand side that says you need a 500A fault current to achieve 0.4seconds disconnection with a 25A MCB!! so don't bother wasting their time tracing lines up tables if they know the current is not sufficient to give a 0.4second disconnection time.
I hope that makes some sense..
As I have had some intoximicating incohlic afflunencing beverages after another busy day at work...
I am sure one or more of my esteemed forumbulator colleagues will correct me,
if I have missed any key points..
Or completely confused myself!!!!!!!
Stay with us Alanz1
And keep asking good questions!